DataMiner System Requirements and Failover system with different specifications
Solved1.73K views8th March 2023DataMiner System Requirements
Miguel Barquet [SLC] [DevOps Advocate]1.92K 22nd January 2021 0 Comments
A customer asked if in a Failover system both DMAs MUST have the same HW specs and even same Windows OS version, or whether a mismatch is acceptable provided they both comply with the DataMiner System Requirements.
Miguel Barquet [SLC] [DevOps Advocate] Selected answer as best 8th March 2023
Ben Vandenberghe [SLC] [DevOps Advocate]9.61K Posted 22nd January 2021 2 Comments
Maybe you can also wait for some further input from engineering, but I would say that this is not a problem.  Of course you have to accept that if you happen to push the boundaries on a beefy primary, you will experience performance degradation when the inferior secondary takes over.  But it’s not like there are dependencies on OS level that requires both to run the exact same Windows OS for example.
Miguel Barquet [SLC] [DevOps Advocate] commented 22nd January 2021
Thank you Ben. That’s what I thought but wanted to double check since I don’t recall seeing such case in Production. We always recommend the same specs for Primary and Backup.
Bert Vandenberghe [SLC] [DevOps Enabler] commented 23rd January 2021
Indeed, that is correct, the specs don’t need to be exactly the same. Just make sure the backup is also able to handle the load when it has to take over. Also note that the load on the database (and HDDs/SSDs) is pretty much the same on the online and offline agent since they both need to store all the alarms and trend data continuously.
