Severity duration is not available for cleared alarms
1st October 2026
If you right-click the alarm in the alarm console and open the alarm card you should be able to traverse the alarm tree and also view its duration.
Answer
1st October 2026
If you right-click the alarm in the alarm console and open the alarm card you should be able to traverse the alarm tree and also view its duration.
1st October 2026
Hi Bernard, Which type of database are you using for the offload? Having a look at the file that is used to create the tables in the remote DB (available …
1st October 2026
Hi Sam, If you have access to the system itself, you can remove the dashboards from C:/Skyline DataMiner/dashboards. Note that this has some caching, so you might have to reload …
30th September 2026
Hi Arvid, The behavior that you are expecting is correct. A trigger will make the time range recalculate its current relative time span based on the current time. It should …
30th September 2026
Hi Sion, I tried this myself and it indeed doesn’t seem to work correctly at the moment. As a workaround, you can use a query filter component which will have …
30th September 2026
There is a hard limit of 1,000 rows. Since you can add a bar/column for every numeric column, the theoretical limit is 1,000 × the number of numeric columns in …
29th September 2026
Hey Cheryl, Changing the baseline value in the row for that element will only impact that specific element. Just keep in mind that Automatically update the baselines is enabled, so …
29th September 2026
Hi Bautista, The 5–10-minute duration suggests that one of the DMAs is entering the Refused state This is an SLNet protection mechanism: other Agents temporarily refuse connections from a problematic …
29th September 2026
Hi Jeyaram, I believe there is already a similar question: Dashboard showing DMA active elements and licenses? Hope it helps.
29th September 2026
This approach requires a large number of joins because I need data from very different tables, and I have to read the inputs on the Appear X multiple times to …
25th September 2026
Hi Caio, An SLDMS NotificationThread RTE means that SLDMS could not process a notification, often sent by SLNet for operations such as file synchronization, within the expected time. This can …
25th September 2026
Hi Samson, here is a documented solution use case which I believe is what you are looking for – Ping Monitoring – DataMiner Dojo Along with the Generic Ping connector …
25th September 2026
Hello Juan, The easiest way is to use our reusable workflow that we actually also use in all our internal work, which handles everything directly. (Unit testing, Building, Upload to …
25th September 2026
Hi Romain, I performed a small test in DMA running version 10.6.8 and was able to make to show the shape based on the service name. In my test, I …
24th September 2026
Hi Samson, I think the Generic Network Services Monitor could be a good fit for this use case. This connector can monitor a wide range of services and protocols, including …