We have multiple elements running the Bridge Technologies VB Probe Series, but despite having alarming disabled for the CC Error Rate in the Service PIDs table, we're consistently getting notices indicating that the Alarm history for this parameter has exceeded 100 alarms.
The only thing I see different is that the parameter has the following configuration:
<Alarm>
<Monitored disabledIf="7019,0">true</Monitored>
<Normal>0</Normal>
</Alarm>
From what I understand, this condition is only applied if the alarm is enabled in the template.
What could be the cause of all these notices?
Hi Daniela,
I see you have trending enabled on this parameter. Can you check if you find any suggestion events for this parameter?
Just add a new alarm tab showing the current suggestion events.
If you find suggestion events in there, you will quickly see if you have entries in there with large alarm trees for that parameter.
If you don't have any current entries, you can of course check the history around the time of the notice.
Hope this helps.