Hello,
I need some advice on Active alarms tab. I have an AppearTV XC5100 chassis with some modules. The AppearTV drivers are loaded up and the Alarm template is defined per module.
I checked all the alarms related to my input module and i have attached the template to the module. At this moment i can see a green dot on my module. This means that there are no actual alarms.
In order to test the alarms, i have created an Input without any content inside. XC5100 chassis is now reporting me a critical alarms with no input. If i go to my view -> XC5100 ip input card -> Alarms section on Dataminer Cube, i can see the alarm listed there.
But there is no alarm on the Active alarms listed on the bottom of the Dataminer Cube app window.
I am still looking into documentation but any advice is welcomed so i can speed up my installation.
The main question for this situation is: How can i be sure that Dataminer will display any alarm that could occur on my device?
Thank you!
Marian
Hi there,
Thank you for picking this up. Initially, i thought that Dataminer will take in all the alarms by default. I was able to see the alarm in the Alarms tab from the DATA section. Please see it in the image below.
But at that moment, i was not able to see the alarm under ALARMS section (just 3 rows under selected Alarms in the image above).
As I am not familiar with the "general" alarms of the Alarming template, i would have expected to have the alarms in ACTIVE ALARMS but ... it was not there.
After i have defined the values in the alarm template, i was able to see the alarm in ACTIVE ALARMS and ALARMS section of my element.
I have been confused by the generality of the alarm so in the begin i had not idea which alarm show i thick in order to get them displayed.
Your indication allowed me to make some changes so it works at the moment. But i have to test this further.
Thank you !
Regards,
Marian