Are manual y-axis range settings in trend graphs stored, and if so, where?
Solved595 views21st October 2025trend Trend Graphs
Catarina Grilo [SLC] [DevOps Enabler]2.96K 20th October 2025 0 Comments
When I open, for example, the trend graph of the Total Processor Load of a Microsoft platform element and change the y-axis from auto range to a manual range (e.g., from 0 to 50), the change is initially applied correctly in the graph.
However, if I close the graph and then reopen it, the manual range is no longer applied, it seems to reverts to the default range defined in the protocol.
This makes me wonder if this setting is supposed to be stored? And if so, where are these settings saved?
Catarina Grilo [SLC] [DevOps Enabler] Selected answer as best 21st October 2025
Toon Casteele [SLC] [DevOps Enabler]7.37K Posted 21st October 2025 0 Comments
The auto or manual preference is saved in your user settings, but the ranges themselves would require a mapping per trend instance for your entire system. This is not supported.
When set to manual range the trend graph will initially either show the range of the parameter in the protocol or, if not available, it will take the outer limits of the trend data y values as its initial range.
Matthias Declerck [SLC] [DevOps Advocate]2.99K Posted 21st October 2025 0 Comments
Hi Catarina,
Y-axis settings on a trend graph in Cube are not saved or stored somewhere. You can set a predefined user setting whether the scaling is done automaticcaly or not based on the data.
The values of the settings are part of the graph itself. This is intended and expected behavior. Any parameter curve can be added or removed on each graph, which make it possible to have same data in different graphs.
Example:
hI hope this help you further
Matthias Declerck [SLC] [DevOps Advocate] Edited answer 21st October 2025