Hi
I am trying to build an alarm point for a specific point in a table which is included in the protocol.
I am trying to use the Index Key as the filter and then the value brought back for severity, the issue is when doing this it wont show as alarm, I have to wildcard the filter, the downside to this is that each row in the table has to alarm for different values in the field.
Is there a way to make this work?
Image 1; This is what I am trying to achieve
Image 2; this is the table with the result of image 1, see the "Select GID" column isnt showing an alarm state
Image 3; This is with the filter Wildcarded
Thanks
Hi Ryan
If I recall correctly, the filter option will use the Display Key of your table to filter things out.
I assume that would be the column TS Input Name [IDX] (given it contains the [IDX] suffix), so could you give it a try with that?
Instead of filtering on 2010000, you could filter on TS Input Switch 1, so it would look something like this: