Hello All,
We have an alarm that has hysteresis set to it on a table. But the row itself only persists for as long as the alarm is active. i.e. when the alarm is no longer present in the system we are monitoring the row is removed.
In this case will hysteresis still work? As the row/column that was alarmed is no longer available. Or with hysteresis should the alarm stay in the Alarm Console for the configured amount of time?
Thanks.
ryan yahia Selected answer as best 24th October 2022
Hi Ryan
The moment your row is removed, the alarm is cleared, despite the hysteresis time.
ryan yahia Selected answer as best 24th October 2022